Re: Hypothetical Light pole.
Bennie: I would be willing to bet that if there was an EGC conductor at the poles, it is probably undersized. A typical installation of a light pole includes upsizing the phase conductors to compensate voltage drop. The problem occurs when 250.122(B) is not followed, and an undersized EGC is installed. You talked about using the conduit as an EGC, and I have no problem with that, but given the potential lenght of the circuit, I wonder what the impedance of the metal raceway is? You can't tell me that having a properly sized EGC would not be better than a metal raceway going a long distance.
Bennie: I would be willing to bet that if there was an EGC conductor at the poles, it is probably undersized. A typical installation of a light pole includes upsizing the phase conductors to compensate voltage drop. The problem occurs when 250.122(B) is not followed, and an undersized EGC is installed. You talked about using the conduit as an EGC, and I have no problem with that, but given the potential lenght of the circuit, I wonder what the impedance of the metal raceway is? You can't tell me that having a properly sized EGC would not be better than a metal raceway going a long distance.