160121-1003 EST
Romex from 1965 12-2 wg is about 19 pfd per foot from hot to the EGC. This would be the uncompensated path for leakage current seen by a GFCI.
With 120 V applied a current of 5 ma results from an impedance of 120/0.005 = 24,000 ohms. Xc = 1 / (2*Pi*f*C). For 24,000 ohms at 60 Hz C = 1 / (6.28*60*24*10^3) = 10^-6 / (377 * 24 * 10^-3) = 10^-6 / 9.05 = 0.11 mfd. At 110,000 pfd to equal a reactance of 24,000 ohms at 60 Hz and 19 pfd per foot the cable length has to be at least 5800 ft long.
It may be possible to trip a 20 A breaker with the above cable at a length somewhat less than 1/4 wavelength at 60 Hz with an unterminated line (open circuit). My guess about 75% of 1/4 wavelength because of the slower propogation in a cable than in free space. 1/4 wavelength at 60 Hz is 186,000 / (60 * 4) = 775 miles.
An open circuit transmission line at 1/4 wavelength reflects back to its input a short circuit. Losses in the line alter this. This is because the reflected signal is 180 degrees out of phase with the input signal.
mivey may be able tell us what a real world power distribution line with an open circuit at about 700 miles would do at the source. Was this part of the problem in the great eastern blackout?
To see the effect at the input of an open circuit transmission line with a low impedance source see my P1 photograph at
http://beta-a2.com/cat-5e_photo.html . The waveform that starts up immediately at the left is the input to the transmisson line. The waveform starting at about 200 nS is the wave at the end of 150 ft of CAT-5E cable.
The free space velocity of light and radio waves is about 982 ft per microsecond. To travel 150 feet would take 0.153 microseconds. Thus, the propogation velocity of the electric wave in the CAT-5E cable is about 77% of the free space rate.
When you look at the input end waveform you see a big rise at about 400 nS. This is the result of the reflected energy from the open end of the transmission line.
Wires in a conduit filled with water will probably somewhat increase the capacitance per foot.