mivey
160121-1003 EST
mivey may be able tell us what a real world power distribution line with an open circuit at about 700 miles would do at the source.
Using about 9400-9500 amps available fault at source:
500 kV A-frame transmission structure:
700 miles: 500 kV at source rises to about 2.5 MV at open end, 5-5.5 kA at source
70 miles: a few percent rise in voltage, 150-165 amps at source
12.5 kV cross-arm MV structure:
700 miles: rises to about 27 kV at open end, 48-50 amps at source
70 miles: a few percent rise in voltage, 3-5 amps at source
480 volt cross-arm MV structure:
700 miles: rises to about 1 kV at open end, 1.8-1.9 amps at source
70 miles: a few percent rise in voltage, 120-130 mA at source
480 volt UG cable:
700 miles: drops to about 63 volts at open end, 2.8 amps at source
70 miles: a few percent rise in voltage, 1.3 amps at source
2000 ft: voltage about the same, about 7 mA at source