Re: Hypothetical
Bennie the reason the NEC require both end to be bonded is because someone can come along and change the water pipe to plastic and then there would be no bond. so they took another route to prevent objectionable current by running a separate grounding conductor that has no current on it. It's like bonding this water pipe and everything else in this separate building back to the main service without any voltage drop. If you use the neutral the voltage drop of the neutral would place current on this water pipe or any else that was common between the two buildings. Which would be bad news for very small wires like telephone, Doorbell, alarm wires, or even a remote garage door opener control wires. That could be a fire hazard.
Bennie the reason the NEC require both end to be bonded is because someone can come along and change the water pipe to plastic and then there would be no bond. so they took another route to prevent objectionable current by running a separate grounding conductor that has no current on it. It's like bonding this water pipe and everything else in this separate building back to the main service without any voltage drop. If you use the neutral the voltage drop of the neutral would place current on this water pipe or any else that was common between the two buildings. Which would be bad news for very small wires like telephone, Doorbell, alarm wires, or even a remote garage door opener control wires. That could be a fire hazard.