I'd like to try to summarize and ask an additional question.
You have a single 120/240 single phase transformer, which will be feeding _30_ panels, each with a 200A main breaker.
The conditions of the installation (outside taps of unlimited length??) are such that you could in principal go from the transformer with 30 conductor sets (each properly protected at 200A) to the 30 panels and meet code, however landing 30 conductor sets on the transformer would not be practical.
You _want_ to run 10 sets of 600A conductors to an intermediate point where you will have power distribution blocks to divide the 10 600A sets to 30 200A sets. The problem is that this 'smells' like a tap of a tap, and doesn't meet the explicit requirements of the NEC tap rules which require a single OCPD at the load end for the particular taps you wish to make.
Is the above correct?
IMHO a 600A conductor protected at the load end with 3 separate 200A OCPD is actually _safer_ then a 'legal' 600A tap protected at the load end by a single 600A OCPD. Because of the way diversity factors accumulate, a panel with a 200A calculated load _likely_ has a real loading that is a smaller % of full capability than one designed at 600A. On top of this, if there is a short circuit downstream of one of the 200A breakers, I would expect lower fault current and lower I^2T on the 600A conductor.
Given the above, if you can show that the design would be 'to code' using 30 separate 200A taps, I think you could make a strong argument to the AHJ to allow a variation and permit the design you actually wish to do. My question: is this a reasonable assessment?
-Jon