I don't know who did this, but...

Status
Not open for further replies.

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
...one of our guys in the field discovered two 25A HVAC units double lugged with 25A wiring onto a single 50A breaker. 25A + 25A = 50A, so that should work, right?
 
...one of our guys in the field discovered two 25A HVAC units double lugged with 25A wiring onto a single 50A breaker. 25A + 25A = 50A, so that should work, right?
Since you post here all the time and I know your experience level I will say :eek:. Otherwise I would say, if they feed fused disconnects at 25A with #10 wire or larger, then it is a valid install.
 
Since you post here all the time and I know your experience level I will say :eek:. Otherwise I would say, if they feed fused disconnects at 25A with #10 wire or larger, then it is a valid install.
I don't think that is the case but I will ask.
 
Since you post here all the time and I know your experience level I will say :eek:. Otherwise I would say, if they feed fused disconnects at 25A with #10 wire or larger, then it is a valid install.
It doesn’t need to be #8 wire between the breaker and the fused disco?

I mean, I understand how #10 could be legit for one HVAC unit, but if there are two on the circuit?
 
It doesn’t need to be #8 wire between the breaker and the fused disco?

I mean, I understand how #10 could be legit for one HVAC unit, but if there are two on the circuit?
Fused disco’s and that would be a tap, but then I remembered a tap has a minimum size so I concede.
 