kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
Why can't they mark it 120-240 volts then? Marking it 120/240 volts would likely mean you can use either but may need to change a jumper or land on different terminals to change voltage.Probably irrelevant. Class 2 means it has to be under 30V and under 100VA. It just goes to the T-Stat then to the "coil", so if you feed it 240V and get 24V, or you feed it 120V and get 12V, it doesn't matter. That "coil" of the relay is likely a newer "universal" coil that's really a little SMPS that puts out 12VDC for the actual coil, accepting anything from 12-30VAC as the input. That's becoming more and more common now.