I have 8 20amp I.G. circuits using #10awg in one conduit from the panel to a pull box. From the pull box we ran 12/2 I.G. mc cable to each of the 8 dedicated outlet locations. I used the approved grounding method of pulling only one ground through the conduit and tying all 8 ground wires to the one ground wire in the conduit at the pull box. Can I do the same with the I.G. (grenn w/ yellow stripe) as I did with the ground wire (green)? My PM is telling me that each dedicated circuits I.G. needs to travel through to the panel. This seems a little redundant carrying 8 I.G's through the same conduit not to mention fill factor. If my PM is correct where is this referenced in the code book. I've looked and can't find anything. Thanks.