I wonder if anyone is submitting a proposal to eliminate the usage of SE cable at 60 degrees. Was there really a problem when it was used at 75 degrees?
infinity said:I wonder if anyone is submitting a proposal to eliminate the usage of SE cable at 60 degrees. Was there really a problem when it was used at 75 degrees?
infinity said:I wonder if anyone is submitting a proposal to eliminate the usage of SE cable at 60 degrees. Was there really a problem when it was used at 75 degrees?
Dennis Alwon said:I disagree--
wireways said:Hey dennis if you are goin to disagree, give code section
iwire said:You have heard correctly 334.80 as Dennis pointed out.
By the way it is not 'derating' it is just 'the rating'
wireways said:Hey dennis if you are goin to disagree, give code section
Thank you 110.14(C)(1)iwire said:New section? :wink: