I have a question about current

Status
Not open for further replies.

Sparky_Dee

New User
Location
Texas
If you have a 4/0 AWG conductor that is connected to a circuit breaker in a 120/208-volt, 3 ph, 4-wire panelboard, how many amps of current can it carry inside the panel?
 

480sparky

Senior Member
Location
Iowegia
Sounds like a test question that's really looking for your knowledge of terminal temperature ratings. But as for the ampacity of the conductor itself, lacking what type of insulation is has there's no possible answer.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Since it's #4/0 I would assume that it's a 75° conductor for ampacity purposes due to 110.14.(C)(1)(b).
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
If you have a 4/0 AWG conductor that is connected to a circuit breaker in a 120/208-volt, 3 ph, 4-wire panelboard, how many amps of current can it carry inside the panel?
I don't get the "inside the panel" part of your question. The code will tell you what the ampacity of the conductor is. It will likely be the same inside the panel as in the conduit running to it, short of the conduit having a bunch of other current carrying conductors in it.
 