Re: i have an EMT question
What would have been the problem with using Intermediate rigid conduit?
There are plenty of quality compression or set screw fittings that are available, for those that do not have threading equipment.
Use the factory threaded ends at the mid span couplings and use a non threaded type connector at one end or the other.
342.30(3)
Exposed vertical risers from industrial machinery or fixed equipment shall be permitted to be supported at intervals not exceeding 6 m (20 ft), if the conduit is made up with threaded couplings, the conduit is firmly supported at the top and bottom of the riser, and no other means of intermediate support is readily available.
Or as has been said use uni-strut, it is not expensive or hard to work with, you can even get it in 20' lengths if you want.
The use of "sealtight" for this application is not allowed, :roll:
350.30(A) Securely Fastened.
LFMC shall be securely fastened in place by an approved means within 300 mm (12 in.) of each box, cabinet, conduit body, or other conduit termination and shall be supported and secured at intervals not to exceed 1.4 m (41/2 ft).
At this point as the LFMC is already run why not run uni-strut beside it and properly secure to that?
[ December 13, 2003, 08:42 AM: Message edited by: iwire ]