I have an inspector failing a job for the main service panel having too many wires?

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
That's a good way to present it to the inspector. "This is the size that it would have to be in order to be at the limit".
IMO the inspector should provide the calculation to prove that the 40% fill has been exceeded. Won't happen but given the blatant display of ignorance it should happen.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
FWIW...
I've noticed that some panels of similar vintage say something on the label along the lines of "This enclosure complies with the wire bending space requirements of the 1980 NEC." Or some such. If the panel label still exists it might be worth peering at it to see if it says anything like that to help you make your case.

(This is not to say that older panels do not necessarily also comply.)
 
Status
Not open for further replies.
Top