Do you have voltage at the ground wire in the CATV box as shown in your photos?
Do you have voltage at the ground wire in the CATV box as shown in your photos?
There is NO ground at the CATV main connection. I'm not sure if I can explain this next part that I forgot to mention in my last post.
With the TV on, on the ungrounded circuit, when I disconnected the cable going to the TV still holding onto the splitter I could feel that tingle you get with some electronics this tingle does go away after a few moments.![]()
plug something in with a load and take voltage readings again. ( a heat gun makes a good load)
Your coax shield is energized. Isolate it from the demark and see if it is then clear. The problem could be coming from another apartment
...and remember this could be the same as breaking a conductive path, creating a potentially lethal voltage differential.
The posted pictures of demarcation indicate the coaxial cables are grounded... i.e. the first splitters on each of the two services appear to be grounded. Having an energized run would indicate that the grounding has failed somewhere.[Edit to add] ...or it may not have been grounded properly to begin with.
I thought the same thing about the grounding at the CATV but when I went into the basement I found the other end of the ground lying on the dirt floor.
The Cable folks are to come back on Tuesday. I'm not sure if I want to be there when they show up.
I thought it looked as if the cable ground might not be truly connected. How many apt. in the building ? What type of wiring method is the building wired with K&T,NM,BX,etc.? ...
I am going to guess one of three things has happened here, 1) the coax has gotten nailed to a phase conductor and accidentally energized. 2) someone has intentionally energized the shield of a coax to make some sort of "bastard circuit" using the shield as the grounded conductor. 3) there is a hot neutral reverse on the circuit somewhere that has energized the coax.
And to add to that for the benifit of the OP - from the sounds of it, all of those interconnected grounds have one path back to the main and bond - the RG-6 from the cable.....All of which have a chassis connection.
If you're reading from any phase conductor to the 'supposedly' grounded shield of the coaxial - you should get a voltage reading from any hot to the shield - unless that 'supposedly' grounded shield is energized by the same leg.... Much like what you are getting from the original outlet - you should be getting the same or simular from the "non-grounded circuit". What is different at that circuit, is that it lacks a path back via the grounded conductor, and a connection for the enegized coaxial.I spent 2-1/2 hrs looking into this problem. This is what I've found.
The suspect outlet is a grounded receptacle. I have tested for voltage as follows: L-N=122, L-G= 122 and N-G=000. So I assume correct polarity. I disconnected the Coax from the Cable Box. This cable goes directly to the demark. When I test from the grounded circuit, suspect receptacle, L-Coax shield=000, N-Coax shield=122 and G-Coax shield=1222.
When I make the same test from a non-grounded circuit I get no readings at all.
I even went to a different grounded circuit, not sure if a different phase, and got the same 122 voltage readings on the Coax connector as well.
I have been using both DMM and a WIGGY. i don't always like the readings from the DMM but I have been able to see specific volt readings with it.I hope you have a DMM, as a wiggy carries voltage and current to the shield of the CATV everytime you test anything hot....
I have been using both DMM and a WIGGY. i don't always like the readings from the DMM but I have been able to see specific volt readings with it.
I hope to get back there tomorrow. This has become a personal challenge and I would like to get it figured out. I really do appreciate all of the help and I'll continue to look for more and of course report back all findings.
Since you already know you have an energized one - take care not to make any corrections to the ground while energized - you don't know what it is energized by yet - it could even be a transformer lead out at the street.....I've been thinking about this for some time as I'm sure you can tell. One of the first questions to the HO was to see if any work has been done in the Apt just prior to the problems. I was told "no".
Just pouring over my notes I noticed that the receptacle that allows the system to work is not only ungrounded it has reversed polarity.
First thing I 'm going to do is correct that problem and start testing again.
I've been doing most of the testing in the Apt. on the second floor and since the panel(s) are outside and about 100' awayI'm going to install my temp. power outlet at the panel and run my cord to the demark. This way I'll be able to change between the "phases" as needed and I'm going to go a head and ground the main CATV blocks.
Wish me luck.
Since you already know you have an energized one - take care not to make any corrections to the ground while energized - you don't know what it is energized by yet - it could even be a transformer lead out at the street.....
Also for what its worth - there may be another point at which the gounding of this could be energized - depending on the configuration - the Telco grounding.
Anyway, I often make line diagrams, even schematics of situations like this to help visualize the problem.... It helps.[/QUOTE]
Bring an easel and a pointy stick also, so you can explain to the tenants what is going on.![]()
Thats for my own benifit - not theirs.... To them I just say "Please remember to reset your clocks...."Bring an easel and a pointy stick also, so you can explain to the tenants what is going on.![]()
Problem solved:
I went back today and after more testing I found the problem.
The suspect receptacle had a "bootlegged" ground formed by a jumper from the neutral to the EGC. I found this the first day, after I removed the jumper I still had a ground and a neutral, so I thought.
I kept testing from line to neutral and line to ground and got voltage so I thought I had correct polarity as well as I had voltage from neutral to coax shield.
After more searching, I found another jumper form the neutral to ECG at another receptacle. When I removed that jumper I found that the neutral was actually the "HOT".
When I corrected the reverse polarity the problem went away.
During all of the testing from receptacles to coax shield I was using the neutral "HOT" and getting voltage on the shield when in reality I was getting the ground from the coax.
It took using the extension cord method coupled with other results from testing that led me to solving this problem.
Thanks to everyone for your insight and willingness to help. I could not have done this with all of you.
Again, thank you to everyone.