Are you saying you have never done work that was covered by the NESC ............
It was a joke dog.
Back on topic, I seem to recall Bob Alexander and Charlie both mentioning ASCR is in a bit of no mans land as far as the NEC.
Are you saying you have never done work that was covered by the NESC ............
Actually, I believe that 310.8(C), (D)
and 310.13, the second paragraph do permit the type of cable 480 installed.
To me this looks like a common farm type service, with the metering at the pole by the garage and feeders feeding the different loads by aerial cable?
We have a few of these around here on farms
Well, to tell you the truth, the ACSR is the least of our worries.
The wedge clamps I used aren't listed either. And I didn't see a NRTL sticker on either that pole or the roof while I was there.
No amount of bathing will cleanse me now.
Joke went over my head.:smile:It was a joke dog.
Back on topic, I seem to recall Bob Alexander and Charlie both mentioning ASCR is in a bit of no mans land as far as the NEC.
No motors, luminaires, TV's, switches, ect. in those pictures. Your NEC golden again pal.
I don't see why it has to be a type listed elsewhere in the code. From Table 396.10(A). (with no Article listed in the right hand column)If that is 'just' ASCR it is not listed so neither 310.8(C) or (D) will apply. ASCR will not comply with 310.11 specifically 310.11(A)(2)
I already mentioned if it was dual rated ....... say XHHW etc. all would be fine. :smile:
Where can I find 'ASCR' in Table 310.13(A) to go along with that paragraph?
The issue would be "identified for the use" as that can be read to require a listing, but it doesn't have to be read that way. It is my opinion that the fact that it is extensively used for this exact purpose makes it "identified for the use".Other factory-assembled, multiconductor control, signal, or power cables that are identified for the use
Identified (as applied to equipment). Recognizable as suitable for the specific purpose, function, use, environment, application, and so forth, where described in a particular Code requirement.
FPN: Some examples of ways to determine suitability of equipment for a specific purpose, environment, or application include investigations by a qualified testing laboratory (listing and labeling), an inspection agency, or other organizations concerned with product evaluation.
..........Why weren't you wearing your "Bee-Suit" making the connection to the line? :smile:
I It is my opinion that the fact that it is extensively used for this exact purpose makes it "identified for the use".
I can't get past how funny post #5 was, I think I cracked a rib laughing
so hard!!!
:smile:
You mean arc flash? No need... the line is dead.
Sorry.......de-energized.
Don, I have not seen any ASCR that complies with 310.11 and I see nothing that relives the requirements of 310.11.
Don, I have not seen any ASCR that complies with 310.11 and I see nothing that relives the requirements of 310.11.
You have seen triplex marked with that info? I never have.I agree they have to be marked as in 310.11, and most of the stuff I have seen was, but where does 310.11 require it to be listed in table 310.13(A)?