detroitelectrician
Member
I am doing a 2 bay oil change and I got a red tag for plugs in customer wait area at 17 inches. The AHJ said they must be above 18 everywhere. There is ventilation of the pit area only (1200 cfm )with 6 air changes per hour. I was told that all conduits thruout must be 18 inches from the floor and 18 from the ceiling. They will not work on any CNG vehicles, is he wrong for requiring all conduits 18 below ceiling?
If the ventilation makes the pit unclassified what areas are still classified?
Thanks for any help or comments
If the ventilation makes the pit unclassified what areas are still classified?
Thanks for any help or comments