In other words, if you need the 15a per circuit, you'd have to use #12 (starts @ 30a), then recalculate the conduit for 14 #12's.Dennis Alwon said:3/4" emt is correct however you must derate based on Table 310.15(B)(2)(a)
14 wires means you must derate 50%
Why do the math? There are tables in Annex C with this all worked out for cases like this where all of the conductors are of the same size and type.OSC16 said:I am trying to figure out what size EMT must I go with to fit 14 number 12 AWG THHN?
So what size EMT should I go with? I have done the math and I have come up with 3/4. Is this right? Please let me know.