Why did people need NEC to clearly specify certain appliances is a cooking appliance in order to be use as a cooking appliance?
OK! 210.19.A.3 For range of 8.75 kw or more rating, the minimum branch circuit rating shall be 40A.
If I have a electric potable stove tap into 40A range circuit should comply with NEC, then why microwave can not?
I'm an electrician, and both comm & res electrical ICC certs.
NEC is for safety, if it's unsafe I'll write correction.
I tried to mention before NEC is not clear on whether or not it considers a microwave as a cooking appliance. If majority of them out there did not have a 5-15 cord cap on them I think they would be treated differently. Problem we have with 5-15 receptacles is you just can not dedicate them to anything - people will plug power strips, multi-tap's, etc. into them to run other items, then you do have a problem as the exception under discussion here is not intended to supply other then cooking appliances. This is before we even get into possible needed overcurrent protection, GFCI protection or AFCI protection, or if an older 120/240 3 wire circuit we have issues with using the grounded conductor for equipment grounding purposes as well.
Next thing that possibly happens is we have this 5-15 receptacle supplied from a 40 or 50 amp circuit and someday someone decides to extend more 120 volt outlets from that receptacle location - now we have multiple 15/20 amp receptacles all tapped into a 40 or 50 amp circuit.
I think maybe the NEC should at least change wording to indicate this tap can only feed 240 volt or 120/240 volt appliances or at least not to supply 15/20 amp 120 volt receptacle outlets. I have a feeling that is the intention here but it is not written all that clearly.
After all that has been said I think maybe I should have been looking for a different code section - how about 210.21(B)?
That would not permit you to directly tap a 15 20 or 30 amp receptacle to a 40 or 50 amp circuit. If you tap and put proper overcurrent protection before the receptacle - it may fly - but now we get into the dilemma that has been brought up before about differences between feeders and branch circuits, and whether or not the overcurrent device has to be a branch circuit protective device or if it can be a supplemental type device. If it is a branch circuit device it must be readily accessible, if it is supplemental is doesn't have to be readily accessible - this is in 240.10.
There is also this in 210.23:
(C) 40- and 50-Ampere Branch Circuits.
A 40- or 50-ampere branch circuit shall be permitted to supply cooking appliances that are fastened in place in any occupancy...
Some microwaves are fastened in place, some are not, most marketed for residential use have a 5-15 cord cap on them anyway. The turbochef ovens or similar mostly found in non dwellings usually have more then a 15-20 amp 120 volt circuit needed and I believe many of those could be tapped onto the circuit in question here.