ptonsparky
Tom
- Occupation
- EC - retired
View attachment 2557752
That's big enough.
What would cause this breaker to not reset? Screwed up mechanism is my first guess. Haven't been there yet and we did not install. I actually thought we were off their vendor list.
New manager says it doesn't even attempt to snap. Load is a soft start for 100 hp motor, I think.
Sometimes the breaker/mech are not aligned and the range of motion is becomes slightly limited.
That is what I suggested over the phone. They didn't think that was the issue...ok.Sounds like they tried to reset it with the door open.
Looks like the instantaneous trip setting anywhere from 1000-2000 amps.What is the Blue dial? any takers on that? It is for my own knowledge. I doubt I ever see this breaker.
I'll second that, and say it appears to be turned all the way up.Looks like the instantaneous trip setting anywhere from 1000-2000 amps.
What I thought but it doesn't. Shunt trip thought was the SS relay shutting the breaker off. IDK.I'll second that, and say it appears to be turned all the way up.
If this is supplying a soft starter I'd expect the soft starter to kick out on LRA before the breaker does.
Is the problem the breaker cannot be reset or not turned on?What I thought but it doesn't. Shunt trip thought was the SS relay shutting the breaker off. IDK.
Not sure if this was resolved already, but if the issue persists (and you can reclose the breaker) there are a few things I would recommend checking (assuming this isn't related to UV release or shunt trip):What I thought but it doesn't. Shunt trip thought was the SS relay shutting the breaker off. IDK.
Isn't that breaker rated for 200A only? Let me know if I am wrong with reason!Looks like the instantaneous trip setting anywhere from 1000-2000 amps.
You're right. I mistakenly put in a 250A frame. Doesn't change much.Isn't that breaker rated for 200A only? Let me know if I am wrong with reason!
Ohh that wasn't regarding to the graph! Isn't that frame is rated for 250A? Why is that breaker has a trip setting of 1000-2000A then? Are these number indicate short-circuit amps, but I think SCA would be at least 14kA at 600V, wouldn't it?You're right. I mistakenly put in a 250A frame. Doesn't change much.
The 200 amp rating is the inverse-time rating, this CB also has an instantaneous trip rating that adjusts from 1000-2000 amps. If at any time the current reached that preset level ( like on motor start-up) the CB will trip.Isn't that breaker rated for 200A only? Let me know if I am wrong with reason!
Unless you're dealing with a motor circuit protector, OCPD's don't just trip at the device rating. The device rating is just the asymptote where the breaker begins to trip, but only after a very long time. As infinity mentioned, we are dealing with an inverse-time breaker which will operate based on the purple curve above. That means the higher the current the faster the breaker will trip (up to a limit - the instantaneous characteristic). The instantaneous characteristic for this device is adjustable (1000 to 2000A range) so it allows you to adjust the lower part of the purple curve.Ohh that wasn't regarding to the graph! Isn't that frame is rated for 250A? Why is that breaker has a trip setting of 1000-2000A then? Are these number indicate short-circuit amps, but I think SCA would be at least 14kA at 600V, wouldn't it?
Most likely to allow the motor to start. Do you know it's normal accelerating time?My tech helped with the clearing and once the mill was clean, the motor started fine.
I do not know the delay between start and trip. IDK why the instantaneous is set so high. We didn’t instal it.