kwired
Electron manager
- Location
- NE Nebraska
To add to what GD said and on a little simpler level (don't know how much you actually know about, you apparently are a student or apprentice of this trade) the typical loadcenter circuit breaker you will find in homes and small business is designed and tested to be able to withstand a 10,000 amp fault. If the supply to the loadcenter is capable of delivering more then 10,000 amps during a fault condition, you probably don't want to be around when that fault happens. Even the 10kA fault that it is supposed to withstand will likely leave you needing clean underwear if you are nearby when such event happens unexpectedly.
When I was in college our class happened to go to Square D's QO breaker plant in Lincoln, NE. This was maybe 1988 or 1989. My favorite point of that visit was the test lab. They let us observe them test a three pole breaker subject to what we were told was a 10,000 amp bolted three phase fault. Don't recall what amp setting the test breaker was, but it had at least 8 or 6 awg conductors on it and all three leads bolted together, snapped into a small loadcenter and closed the heavy doors on a bigger vault. Then turned on the power - "BOOM". opened the vault door and smoke was still rolling out of the loadcenter. Reset the breaker, and it did physically operate though it looked like something you wouldn't want to ever use again.
When I was in college our class happened to go to Square D's QO breaker plant in Lincoln, NE. This was maybe 1988 or 1989. My favorite point of that visit was the test lab. They let us observe them test a three pole breaker subject to what we were told was a 10,000 amp bolted three phase fault. Don't recall what amp setting the test breaker was, but it had at least 8 or 6 awg conductors on it and all three leads bolted together, snapped into a small loadcenter and closed the heavy doors on a bigger vault. Then turned on the power - "BOOM". opened the vault door and smoke was still rolling out of the loadcenter. Reset the breaker, and it did physically operate though it looked like something you wouldn't want to ever use again.