- Occupation
- PE (Retired) - Power Systems
You need the real data, I have nto dealt with Excel but I have with many other utilities and it is usually just a matter of contacting the right person. Many have an engineer assigned to provising this data to engineering firms doing arc flash studies.
Xcel Energy, provides one set of fault current values for determining the AIC of protective devices and the SCCR of equipment.
They provide a different set of values for use in arc flash calculations. They also recommend that you perform arc flash calculations using at least one size larger and one size smaller transformer and then base your PPE on the worst case scenario.
This is not a case of contacting the right person. Xcel only provides realistic values to 'secondary service' customers that are extremely large. I would guess I get 480V fault values for about 10% of my Xcel customers.