ICF (Insulated concrete forms)

Status
Not open for further replies.

cschmid

Senior Member
when wiring ICF's is NMB allowed? How would we be able to classify NMB protected in Styrofoam? with the form only being 2" thick is it conceivable to say that in order to remain 1 1/4 inch's in Styrofoam you could do it as to never be exposed to the concrete? Just curious since it is new building method and not covered in the NEC that I have seen.
 
I looked for NM-B in 334. and that was not even listed. Someone straighten me out...
334.10 (B)(2)- ... not used ... where embedded in masonry,concrete, adobe fill or plaster.

Any one that been below the boarder and in the out back that's exactly what they do with there Adobe's... :roll:
 
oops just NM sorry about the extra key must do better job of proofing.....

you know the wire you use everyday when you do residential, like the wire you get from HD, Lowe's, Menards...you know the wire home owners buy.
 
I'm giving you the benefit of the doubt about your qualifications to perform electrical work, but if you dont understand the difference between NM and NMB than im wondering what sort of training and licensing you had...
 
I'm not sure that I understand the question. Do you want to run the NM cable within, in front of, or behind the Styrofoam? Also the 1 1/4" separation is from the edge of a framing member.
 
jamesguy10 said:
I'm giving you the benefit of the doubt about your qualifications to perform electrical work, but if you dont understand the difference between NM and NMB than im wondering what sort of training and licensing you had...


There are countless people in our industry who are good electricians or ECs that are unaware of what the B in NM stands for. Some actually would not even know what NM means, as "Romex" is the nomenclature they are accostumed to.
 
A simple question of whether you can running NM in ICF's is code? degrades into cheap shots. wonderful good morning to you too... I make a good living doing this and have had one change order from the inspector in 20 yrs and It was not even my work and he made me fix something already installed by someone else. so snide remarks wont affect my pay or credibility with the inspectors here. so have a nice day and later on.
 
ICF's?

ICF's?

cschmid said:
A simple question of whether you can run NM in ICF's is code?

What about UF-B?

Are you talking about the styrofoam blocks that go between pours? Or is this the insulation that goes underslab?

Will it go through the pour? Whats ever been wrong with smurf tube? That stuff is pretty cheap and allows for future flexibility like adding ckts.
 
I am currently having an ICF home built for myself. I believe I can use NM in the walls. It will have to be chased 1 1/4" into the wall pr provided with some type of mechanical protection. We build a lot of adobe around here, and NM isn't permitted in those walls, they are considered hygroscopic by nature.

Jim T
 
we recently did a resort that was like that. what we did was take a heat gun with a pencil tip and melt a groove into the foam, be carefull as this stuff melts QUICK. then just stuff your wire into the groove and cover it with clear packing tape. worked out really sweet. also your boxes will give just the right amount of reveal just take a sheet rock saw and cut the foam then anchor to the concrete.
 
Good after noon I did do a typo last nite on the NMB I have discovered that being that specific with the wire, we would not look at the other aspects. Now I will tell you a scenario. Last year one of my co-workers a civil engineer built a new house and he had a ICF basement under it. These insulated concrete forms (ICF) are Styrofoam with plastic nailer built into the foam every 16 & 24 inch's. the nailer's are only 3/16 to 1/4 of an inch thick; depends on brand. He wired his in EMT and when the inspector inspected it, the inspector told him he could of saved some cash by using NM. I was shocked because the only way I can see being able to run nm is by cutting a grove in the foam and I do not see how foam provides protection from physical damage. if you cut a groove in wood you have to cover it with a steel plate. that would be impractical in foam. how would you secure it? romax staple in the foam, that does not sound like it would hold to me. I do not see any way of drilling it. So I was wondering what others have found working with it? I was also curious of if anyone here sat on a committee that has discussed this new building practice? I know it is catching on fast here and I can see real growth in that area of construction, especially in the commercial arena.
 
jamesguy10 said:
I'm giving you the benefit of the doubt about your qualifications to perform electrical work, but if you dont understand the difference between NM and NMB than im wondering what sort of training and licensing you had...

You give me nothing; because you have already judged me.....I earn everything.
 
I am asking my electrician to groove it at least 1 1/4" deep and then fill the groove with sealing foam. I am using RASTRA which has concrete filled tubes inside the foam, but no nailers available.

It is catching on, but still costs a bit more to construct. I am in love with the 12" thick walls, the super insulation, etc.

I've designed electrical in commercial buildings built with RASTRA, but we were required to use EMT because of local codes forbidding NM in any commercial buildings.

Jim T
 
I am buying RASTRA from a local distributor. I live in southern NM, and RASTRA is built in Juarez Mexico, about 45 minutes away, and also somewhere in Az. I'm sure there are other plants, but these are in my area.

I can't really judge how much more it costs in my home, I didn't bid framing to compare. The cost for RASTRA blocks for all exterior walls in my 2300 sq ft home including a 14' wall in the great room was $15K. This doesn't include concrete, rebar, installation, etc.

I've heard ICF costs about 10%-15% more around here.

Jim T
 
The cost of ICF's here run any where from 17 - 20 dollars a square ft. concrete walls are measure differently then the square footage of a house. It is lenght times height of the wall and the price is also dependent on thickness.
 
Right, thanks on the Typo notice, you made me go read da book :rolleyes:

Interesting articles on its usages and it was described in reference to your OP, if you hold it to class per article. N/A
It wasn't the way I remembered it either, maybe ...
I don't personally like the app / but "OK", somethings going there.

I just can't see working a wall with any of the mentioned tools to install circuits and box out. Hot stick, Dremels, large knifes :) I better get over it
 
I wired ICF homes in the earley 90's in Florida. You guys are putting way too much thought into this. I used an electric charcole lighter to cut about 3/4 to 1" grooves down the walls. Used nails to hold it in place just as you would staples down a stud. When you wire rx down a wall, it is in the 3/4 air space between the drywall and the block so why would you need a deeper grove in ICF? In my case, the furring strips were screwed to the walls with tapcons. I just stayed away from them except to get to the boxes. No furring strips to cut or notch, No kick plates to install. No blocks to beat holes in, No foam needed.
 
I am truthfully sorry for misjudging you. Sometimes i forget that things are different in other parts of the country. Its just that around here there is a lot of NM in older homes, opposed to NM-B, and everyone around here (thats licensed anyways) knows the difference because we use the terms in everyday discussions.
 
Does anyone have a photo of an ICF installation? Are these typically finished with drywall? If so what it the drywall attached to?
 
Status
Not open for further replies.
Top