gporter85
Member
- Location
- Merced, CA
I like the ideal of a 600A rated busbar with 400A OCPD also. This would allow me to use a breaker in main panel as my disconnecting means instead of a disconnect outside. My local PO allows us to waive the requirement for the manual disconnect switch.
To prevent a net metering customer from back-feeding a de-energized line, the customer
shall install a manual disconnect switch with lockout capability that is accessible to
Company personnel at all hours. This requirement for a manual disconnect switch will be
waived if the following three conditions are met: 1) The inverter equipment must be
designed to shut down or disconnect and cannot be manually overridden by the customer
upon loss of Company service; 2) The inverter must be warranted by the manufacturer to
shut down or disconnect upon loss of Company service; and 3) The inverter must be
properly installed and operated, and inspected and/or tested by Company personnel
I have done a lot of work in CA. PG&E the main utility has no problem whatsoever tapping any service. Be it double lugs on the line side of a disconnect between meter and Switch, Polaris lugs or IPC's. Some of the smaller utilities that are local irrigation districts want a UL inspector on site to watch you perform the tap... To a tune of $5-10,000. In that case having a custom panel built to accommodate the 120% rule is less expensive and easier. But every single commercial job i have ever installed has required knife blade disconnects fused or not.