The lead lined tile shower IS producing the voltage. The voltage must be being produced through a chemical reaction between the grout, the lead and the copper. As absurd as that sounds

Where were you connecting your voltmeter to get this reading?
 
The voltage must be being produced through a chemical reaction between the grout, the lead and the copper. As absurd as that sounds .
I don't think that is possible. The galvanic reaction voltage between lead and copper will only produce ~0.2 volt per cell. I don't think that there is any way the you have the 115 copper/lead cells in series and that is what would have to take place to produce 23 volts.
Don
 