pipe_bender
Senior Member
- Location
- Boston
- Occupation
- Electrician
the way I read it if there are one or more three phase systems and a split phase system in the same building one can use the same color for each leg of the split phase system.Article 220 explains the systems
(A) Voltages. Unless other voltages are specified, for purposes
of calculating branch-circuit and feeder loads, nominal
system voltages of 120, 120/240, 208Y/120, 240, 347,
480Y/277, 480, 600Y/347, and 600 volts shall be used.
120/240 is one system as far as the NEC is concerned not to mention the physics of one center tapped winding.