Hello,
Could someone possibly explain how the "Actual Voltage Drop" formula (page 98 of IEEE 141-1993) is derived from the phasor diagram on the previous page?
Vd = es + IRcos(theta) + IX sin(theta) + sqrt(es^2 - (IXcos(theta) - IRsin(theta))^2)
I realize it does not take into account temperature variances and more detailed evaluation of magnetic fields. However, in a basic voltage drop, I would have approached it differently.
The IEEE equation assumes we know the current. If that is true and we know the value of R and X of the cable based on 1000 ft., then we can calculate voltage drop without even needing to know the source voltage, es.
Zcable = R + X
VdropL-N = I * Zcable
Vdrop_1phase = I * Zcable * 2
Vdrop_3phase = I * Zcable * sqrt(3)
If one uses the longer version the standard provides, I find it more confusing when you assume there is unit power factor (ie: cos(theta)= 1 ...sin(theta)=0)
You will be left with the following equation:
Vdrop = es + IR + sqrt(es^2 - IX)
If you have unit power factor, there should be no reactance (X).
Thank you all for taking the time to explain or further disprove the IEEE 141 method for cable voltage drop.
Could someone possibly explain how the "Actual Voltage Drop" formula (page 98 of IEEE 141-1993) is derived from the phasor diagram on the previous page?
Vd = es + IRcos(theta) + IX sin(theta) + sqrt(es^2 - (IXcos(theta) - IRsin(theta))^2)
I realize it does not take into account temperature variances and more detailed evaluation of magnetic fields. However, in a basic voltage drop, I would have approached it differently.
The IEEE equation assumes we know the current. If that is true and we know the value of R and X of the cable based on 1000 ft., then we can calculate voltage drop without even needing to know the source voltage, es.
Zcable = R + X
VdropL-N = I * Zcable
Vdrop_1phase = I * Zcable * 2
Vdrop_3phase = I * Zcable * sqrt(3)
If one uses the longer version the standard provides, I find it more confusing when you assume there is unit power factor (ie: cos(theta)= 1 ...sin(theta)=0)
You will be left with the following equation:
Vdrop = es + IR + sqrt(es^2 - IX)
If you have unit power factor, there should be no reactance (X).
Thank you all for taking the time to explain or further disprove the IEEE 141 method for cable voltage drop.