IEEE Standards Dictionary
charlie b
Lockport, IL
Retired Electrical Engineer
Can anyone who has access to this document tell me whether its definition of "manhole" is such that a vault that sits under a transformer would meet that definition?
190613-1303 EDT
charlie b:
I might expect the University of Washington would have a similar connection thru their library. It may be that if you visit their library that from the library computers that you may be able access IEEE Explore. Check with the EE department at U of W.
Sorry for my tardy reply. This is from the IEEE Std 100 - 1996 edition:
manhole (1) (More accurately termed splicing chamber cable
vault) A subsurface chamber, large enough for a man to enter,
in the route of one or more conduit runs, and affording facilities
for placing and maintaining in the runs, conductors,
cables, and any associated apparatus. See also: splicing
chamber. (PE/T&D) [10]
(2) An opening in an underground system that workmen or
others may enter for the purpose of installing cables, transformers,
junction boxes, and other devices, and for making
connections and tests. See also: distribution center: splicing
chamber. (BT) [34]
(3) A subsurface enclosure that personnel may enter used for
the purpose of installing, operating, and maintaining submersible
equipment and cable.
(NESC/T&D) C2-1997, C2.2-1960
I have always treated the vaults you described as "manholes" in my refinery experience.