It also assumes the same efficiency, and the same I2R losses in both the stator and the rotor.
drcampbell Senior Member Location The Motor City, Michigan USA Occupation Registered Professional Engineer Jul 2, 2019 #41 It also assumes the same efficiency, and the same I2R losses in both the stator and the rotor.
StarCat Industrial Engineering Tech Location Moab, UT USA Occupation Imdustrial Engineering Technician - HVACR Electrical and Mechanical Systems Jul 2, 2019 #42 Hey dave Hey dave ActionDave said: Depending on the load and the motor a 230V motor will most likely run just fine on 208V. Until a motor is loaded it will draw lower amps at lower voltage. I know that is not what everyone says but it is true. If your motor is not loaded to the max and the manufacture says it is ok then I would have no problem trusting what they say. Click to expand... That is one fine Tabby Cat.
Hey dave Hey dave ActionDave said: Depending on the load and the motor a 230V motor will most likely run just fine on 208V. Until a motor is loaded it will draw lower amps at lower voltage. I know that is not what everyone says but it is true. If your motor is not loaded to the max and the manufacture says it is ok then I would have no problem trusting what they say. Click to expand... That is one fine Tabby Cat.
kwired Electron manager Location NE Nebraska Jul 3, 2019 #43 kwired said: We don't really know if OP's 47 amp motor is full load rated for 47 amps or if that is what it typically draws when in use. Click to expand... Besoeker3 said: exameninto Click to expand... After recent OP posts, it appears the 47 amps was the required minimum conductor ampacity for the unit - already has 125% of largest motor rated amps included in that figure. Actual full load rating was 41 amps - at 230 volts.
kwired said: We don't really know if OP's 47 amp motor is full load rated for 47 amps or if that is what it typically draws when in use. Click to expand... Besoeker3 said: exameninto Click to expand... After recent OP posts, it appears the 47 amps was the required minimum conductor ampacity for the unit - already has 125% of largest motor rated amps included in that figure. Actual full load rating was 41 amps - at 230 volts.