What does that have to do with the question?Chapter 9, note 4, in your case yes.
If you want to follow the letter of the code all conduits, no mater how short, require a support and in the case non-flexible conduits the conduit terminations are not supports. In most cases the inspector will permit 2 to 3' of straight non-flexible conduits to be be supported by the conduit terminations, but that is not what the code says.
If you want to follow the letter of the code all conduits, no mater how short, require a support and in the case non-flexible conduits the conduit terminations are not supports. In most cases the inspector will permit 2 to 3' of straight non-flexible conduits to be be supported by the conduit terminations, but that is not what the code says.
Same here. I have brought it up before, sometimes putting it to some extremes to make the reality set in better, like if I put a strap on a 30 inch long piece of 4 inch RMC between two cabinets, and well secured to each cabinet, does the strap support the RMC or does the RMC support the strap?:roll:I agree that's what the NEC says even if I think that it's dumb.
Got me all confused, your mentioned note 4 is about raceway fill, OP question was about raceway support.Your weekend to watch me, Don?
Was it the fact that I stated a Chapter 9 Something as opposed to an actual Article of work to be completed by the OP's question?
Why such a comment, The Index say Nipples, conduit,see Conduit nipples.
Conduit nipples Chap. 9 Note 4.
Let me assume the the OP thinks they have a nipple application, either by minimal length or not understanding the length of when it's a nipple or not.
They said pipe, let me assume EMT, but not RMC, or flex or you stated.
To the OP you need two means of mechancial fastening? You the OP do not have the luxary of 60 percent fill that the 2'-0? nipple would provide, IE run some more pipe (EMT) or what ever you choice is of raceway is (assuming something round!)
Same here. I have brought it up before, sometimes putting it to some extremes to make the reality set in better, like if I put a strap on a 30 inch long piece of 4 inch RMC between two cabinets, and well secured to each cabinet, does the strap support the RMC or does the RMC support the strap?:roll:
Got me all confused, your mentioned note 4 is about raceway fill, OP question was about raceway support.
If you want to follow the letter of the code all conduits, no mater how short, require a support and in the case non-flexible conduits the conduit terminations are not supports. In most cases the inspector will permit 2 to 3' of straight non-flexible conduits to be be supported by the conduit terminations, but that is not what the code says.
The code for unsupport/non-secured wipes only apply to light wipes of 6' or less.
But that section has nothing to do with support and everything to do with raceway fill, the OP's question is about support not fill:?If you over 24" you can make me out to be an ass as you do always , chap 9 note 4 is what I stated don't read to much into it.
Given the fact that the code specifically permits a raceway termination to be used as the raceway support for flexible raceways used as fixture whips, it is my opinion that the use of raceway terminations as the required raceway support for other applications is not permitted....
If anything we need to ask what kind of raceway it is before we can accurately answer, but for the most part unless it is a flexible raceway, the first support of almost all other raceways needs only to be within 3 feet of the raceway termination, ultimately making the question become does a second termination within three feet of the first require additional raceway support or can the termination method(s) be considered the support?
I'm trying to figure out how I'm going to support a close nipple if support is required no matter how short the conduit run. Same goes for offset nipples.
Mark
This very question was submitted as a proposal for the 08 code, the CMP twisted it all around, and then it was removed from the 2011 NEC.
Most say closer than 3 feet don't need support but a close reading does not support that.
What does the word wizard, Charlie B say?
(He applies logic and reading rules to the NEC)
If there is no structural items in that distance to attach to then why not use the exception?What of the exception for emt and some others. Emt specifically NEC 2011 358.30(A) exception No. 1. where it can be increased to 5ft.
The exception does not eliminate the requirement for a support...it just permits the support to be at 5' in place of the general rule requiring it within 3'.What of the exception for emt and some others. Emt specifically NEC 2011 358.30(A) exception No. 1. where it can be increased to 5ft.