Installing filters or surge suppressors that have caps or MOVs connect to ground at the equipment is a bad idea! But, count-less people continue to do it!
Not people, manufactures. They have no choice to meet FCC requirements.
The solution is really easy and the problem stems from the US electrical architecture of using grounded 120 VAC unbalanced systems. One simple solution is to use equipment that uses 240 VAC rather than 120. All the noise problems are gone due to the balanced nature of 240 VAC.
Another solution I ran across years ago when doing electrical work in recording studios, and later used in Data Centers is Balanced 120/60 distribution covered in NEC 647.
However today it is pretty much all academic as ground referenced signal transmission is antiquated and resides in history books. For those systems still employing ground referenced signal transmission, there are much better effective techniques to use than IGR.