Not familiar with these connectors, do they by chance make any that are IPC on one port but not the other?
Otherwise isn't a main concept of using them is to lessen potential contact with live conductors, which means it wouldn't be a big deal to strip a grounded conductor to terminate it?
How you handle your own grounded conductor is not the issue in question. The issue is how you handle the tap to the existing grounded conductor that lacks insulation, when you planned on using the insulation connector for the neutral as you planned for the ungrounded conductors.
My recommendation if using these on the insulated existing service conductors, is to avoid them for the bare neutral, and use a 3-port insulated tap connector instead (commonly called a Polaris connector). One port to intercept the existing conductor, a second port to reconnect it to its original destination, and a 3rd port for your tap.
The purpose of using these insulation piercing connectors connectors, is so that you can leave the feeder conductors connected to the terminals of their existing destination, and provide a connection to the insulation. These are analogous in concept to saddle valves in plumbing (something I recommend against ever using, and many state plumbing codes prohibit). But the electrical counterparts of insulation piercing connectors, do not suffer form the same issues, and the NEC and UL listing should make them legal to use in theory.