The resistance of the human body can vary dramatically depending on several factors. Essentially it is the skin, along with such factors as area of contact, tightness of contact, dryness or wetness of the skin, and cuts, abrasions, or blisters that introduce the variables.
Excluding the skin, human body resistance is about 250 Ohms per arm or leg, and 100-500 Ohms for the torso. The more muscular the person, the lower the resistance. Unless the skin is punctured, the skin will provide additional resistance. The worst-case scenario is considered to be 500 Ohms hand-to-hand. Some typical values of skin resistance are:
Condition of contact Resistance (Ohms)
Dry Wet
Finger touch 40 k-1 M 4-15 k
Hand holding wire 15-50 k 3-6 k
Finger-thumb grasp 10-30 k 2-5 k
Hand holding pliers 5-10 k 1-3 k
Hand around pipe (or drill) 1-3 k 0.5-1.5 k
Palm touch 3-8 k 1-2 k
Two hands around pipe 0.5-1.5 k 250-750
Hand immersed -------- 200-500
Foot immersed -------- 100-300
Using these typical values, a person can estimate their approximate body resistance. Let?s say a person grabs a wire in a 480/277V panel that they assumed was deenergized while touching the panel door with the other hand. The worker would have about:
250 ohms for the arm +
250 Ohms for the other arm +
32,500 Ohms for the skin
A total resistance of about 33,000 Ohms
277V/33,000 Ohms = 8.4 mA (Mild shock)
Now lets look at the same scenario, but this time with wet or sweaty skin.
4500 Ohms for the skin
A total resistance of about 5000 Ohms
277V/5000 Ohms = 55.4 mA (Respiratory Paralysis, possible fibrillation, may be fatal)
At voltage levels above 600V, the resistance of the skin ceases to exist; it is simply punctured by the high voltage. For higher voltages, only the internal body resistance impedes current flow. At levels about 2400V and higher, burning becomes the major effect, lower voltages fibrillation and asphyxiation.
How well you are grounded is also a factor. Wearing rubber soled shoes or gloves along with the material between you and ground will add to your total resistance. Some typical values for different materials:
Materials Resistance (Ohms)
Rubber gloves or soles More than 20 M
Dry concrete above grade 1-5 M
Dry concrete on grade 0.2-1 M
Leather sole, dry 100-500 k
Leather sole, damp 5-20k
Wet concrete on grade 1-5 k
(Resistance values for equal areas (130 cm2) of various materials)