I'm not finding the file.
joe tedesco said:Go to www.nema.org and see the ppt file identified below on how fittings are supposed to be installed.
The use of fittings used improperly is the issue!!
MDShunk said:That is the latest puzzle, indeed. Joe Tedesco brought this to light a couple of months ago. There are, indeed, fittings designed expressly for this purpose. People often call these "combination couplings". It would be a fitting designed, in this case, to change from EMT to FMC, without using a RMC coupling.
This information was related to me this morning from Scott Cline, Chairman of NFPA 70 (NEC) CMP 6, about a very similar installation:
Q: The installation shown in the image is not the intended application or
listing recognized by Underwriters Laboratories (UL) and VIOLATES 110.3(B).
A: My U.L. Code representative disagrees with you. He sees no violation of
listing. Given that the connector/locknuts are properly tightened, the application meets the listing.
Q: As I interpret this picture there is a malleable iron squeeze type connector
securing the flexible metal conduit. On the other end is a steel set screw connector assembled to EMT. Both connectors are joined to a coupling with the connectors locknuts made up tight (?) to the coupling.
A: We agree as to what the picture shows. (Any application is reliant on proper workmanship regarding tightening of the parts. Unless egregious, a picture cannot show a failure to properly torque.)
Q: First, a connector cannot be used as a coupling unless so listed.
A: The connector is not used as a coupling; it is used as a method of connecting its raceway to the thread of the coupling.
Q: Second, connectors have not been UL tested for resistance or ability to carry potential ground fault current when assembled to a coupling.
A: Connectors ARE tested for application to threaded connections. The mating threads of the coupling and the threads of a conduit body, etc., are the same.
Q: Third, the threads of the connectors may not match those of the coupling
raising the risk of connector pulling out of the coupling.
A: The male and female threads of electrical fittings are all made to the same
NEMA standards. They are specifically made this way so that the installation of various parts and various brands will mate properly.
Q: Fourth, there is no assurance that locknut(s) will not loosen.
A: The assurance of a locknut or of any fitting not loosening over time is proper installation workmanship. This is irrelevant to the various allowable combinations of fittings.
Q: A better choice for this installation would have been couplings designed and listed for the application. Fitting manufacturers such as O/Z-Gedney offer such a coupling for trade sizes 1/2" EMT - 3/8" FMC up to 2" EMT - 2" FMC; Bridgeport Fittings has sizes 1/2" EMT - 3/8" FMC up to 1"EMT - 1" FMC.
A: Single-purpose fittings such as those you mention would certainly be
appropriate. They might even save on installed cost, but they are not the only correct solution.
Mr. Cline offers the following, in summary:
The pictured installation does not appear to show a violation of 300.10's requirements for metallic continuity. It does not appear to show a violation of 300.15 in general, or 300.15 (F) in particular. It does not appear to show a violation of 358.42. Indeed, the screws and the connector's main thread/locknut appear to be fully seated.
Now that I offer that opinion of one man, I offer you this commentary of my own. Mr. Cline's opinion appears to run counter to NECA 1-2000, NEMA RV-3, NEMA FB2-10, and NEMA 2-20.
We'll just have to wait and see how this plays out in the end. It's causing quite a stir in the mean time.
joe tedesco said:Let's just say that we are in the minority here, and that some feel that they can mix and match listed fittings anyway they want in spite of 110.2!
Comments about NEMA, not being an authoritative source are hilarious, and the members of the NEMA companies will agree with us, and others here who are aware of the poor workmanship.
The issue is one clearly defined - use the proper fittings for the purpose intended.
Who from the Inspection Community agrees with the opposition here?
Question:
Can anyone show us the text and images and training guides in the materials from the union and non-union shops that teach the methods shown in the picture?
kingpb said:I know you guys have been beating this around a while, what I am wondering is how is it all supported? Doesn't the felxible conduit need to be supported within a certain distance of the coupling to keep it from wanting to pull the set screw connnector from the EMT. Is the EMT set screw connector designed for supporting the coupling/flex assembly?
joe tedesco said:Ryan:
I thought that there was some proposal to remove references to the NECA pubs?
If you totally ignore them, particularly NECA 1, what on earth do you use for 110.12 guidance?ryan_618 said:Joe, I'm sure we both agree that the NECA documents aren't enforcable code, right?
I don't use anything. If the installer follows the prescriptive rules of the code, such as for securing and supporting, I pass the installation. 110.12 is far too subjective, and does not create any safety hazards.mdshunk said:If you totally ignore them, particularly NECA 1, what on earth do you use for 110.12 guidance?
I do absolutely agree that is it subjective when no other guiding text is referenced.ryan_618 said:110.12 is far too subjective, and does not create any safety hazards.