iwire said:But if many of the conductors simply pass vertically from the top raceways to the bottom raceways that will not be an issue.
That would be right for metal wire ways, Nonmetallic and aux gutters covers all conductors.
"The derating factors specified in 310.15(B)(2)(a) shall be applicable to the current-carrying conductors up to and including the 20 percent fill specified above."
It also covers all conductors .
378.22 Number of Conductors.
The sum of cross-sectional areas of all contained conductors at any cross section of the nonmetallic wireway shall not exceed 20 percent of the interior cross-sectional area of the nonmetallic wireway.