i wouldnt even consider in a hundred years not using al here. they sell 100amp mobile home feeder 2-2-4-6 for a buck and a half a foot, no pipe, no box, no probs.
iwire said:What code section requires a listing for hand holes? :-?
barbeer said:I only know of 110.3.........why would you ask that? (I thought the answer would have been assumed:roll: )
barbeer said:I guess you could run with 314.15 as well.
barbeer said:Any speculation of why an inspector in 2002 would ahve required us to have them listed?
jbt260 said:Many AHJ's require equipment to be listed. This falls under 110.2 and the definition of "approved".
jshaw said:Can someone tell me where the code specifically states that the interior of underground conduit is designated as a wet location?
jbt260 said:Also, in a previous post, THHN was mentioned. UG conduit is considered wet location. THHN cannot be used.