FWIW in Canada 8/3 has been allowed for some time on 50 amp range circuits.
FWIW in the US
Note 4 to Table 220.55 would allow you to power a Household range up to 13kw on a 40 amp circuit.
FWIW in Canada 8/3 has been allowed for some time on 50 amp range circuits.
Note 4 to Table 220.55 would allow you to power a Household range up to 13kw on a 40 amp circuit.
FWIW in the US
Correct, however the CEC has no 60*C restrictions for NM like the US.
Probably because 75% of the NM in Canada is operating below freezing (joke)
No, it was not in the code, just some guys noticed the new spec for NM-B and thought that meant they could treat it the same as other 90 degree conductors.Was this in the code?
No, it was not in the code, just some guys noticed the new spec for NM-B and thought that meant they could treat it the same as other 90 degree conductors.