I have a general question about Incident Energy levels and how they can possibly change as you work your way through the circuit. My specific situation is I have a known arc flash rating at some 480V distribution panels. The arc flash rating at those cabinets is only about 0.5 cal/cm2. These cabinets then feed various cabinets of HFPS's. The question I have is can it be safely assumed that the Incident Energy rating of the HFPS cabinet is less than or equal to 0.5 cal/cm2? Or is there a possible scenario where it could be higher than that? Appreciate all the insight here.
It can go either way. It depends on what is going on. First although you stated 480 V I need to clarify that transformers matter. Normally incident energy goes up downstream of a step down transformer. That is except for ones with very high impedance (control power transformers, instrument transformers). 1584 gives a cutoff short circuit current for this.
This is until it gets to such a low voltage that incident energy calculations don’t apply, roughly under 208 V.
Then we need to look at whether the “trip device” is “definite time”. This is the case when the short circuit current is in the “instantaneous” trip region of a device or it is at 2 seconds or the device trips after X seconds regardless of current. In this case as we would expect as distance increases cable impedance increases so short circuit current decreases, thus arc power decreases but since opening time is fixed, incident energy decreases.
If however it is in a trip curve region regardless if it is a fuse, a breaker, or something else, as the short circuit current (hence arc power) decreases, it also extends the time needed to trip. On nearly all devices it is going to increase the opening time faster than the decrease from short circuit current so we get a net increase in incident energy. This is counterintuitive but is what happens. It does not happen with very slow devices but these are rare.