Not an NEC Issue. It's a design issue
If the heat pump is locked out at lo temp and they go to electric heat then use the larger of these two loads heat pump or electric.
If the electric heat is used for reheat (they do this for humidity control sometimes) then you have to carry the whole load.
If they are reheating already cooled air their not supposed to it's against the energy code unless it's a temperature and or humidity controlled room like a computer room or lab
If the heat pump is locked out at lo temp and they go to electric heat then use the larger of these two loads heat pump or electric.
If the electric heat is used for reheat (they do this for humidity control sometimes) then you have to carry the whole load.
If they are reheating already cooled air their not supposed to it's against the energy code unless it's a temperature and or humidity controlled room like a computer room or lab