I am wiring an office space. The plan calls for branch circuit conductors to be increased by one wire size for every 75' of length to meet the provisions of no more than 3% voltage drop on any branch circuit per the FBC.
Is that a requirement or just an architect covering his butt.
Would that mean measuring every conductor in every conduit and cable and making an increase for every 75'? Or would it be for each device over 75' from the panel?
Would I have to use over sized cable at switches and receptacles? Or just home runs?
I am going to be careful here. I live in Florida. I see similar notes all the time. I almost never see it complied with to the letter. As stated it is a code in Florida that VD for branch circuits can not exceed 3%. So that would be what I consider etched in stone.
It is a rare circuit indeed that would exceed 3% at 75 or even 100 feet. If you bid a job or install a job ignoring a requirement like that from an Engineer then they would be within their rights and they would win, to force you to correct it, or provide a credit. If you bid your jobs with it fully accounted for, you will not likely win very many.
Example. One of the best, and I mean that I respect their ability and the thoroughness of their design, has a similar statement. On one job, they issued a change order to relocate the panels 25 feet further from its location. I issued a change request that accordingly increased the wire size of virtually every conductor. The price choked everyone, so of course, I was asked to justify it. I explained and the answer was, "our requirement is more stringent than it needs to be and an increase will not be necessary."
I know that when I do a job that they designed they expect 3% not to be exceeded. They don't worry too much about the rest.
Take all of that or leave it. If you work under someone else's direction I recommend you discuss it with them and follow what they tell you.