If I have a 480V 6 lead motor that is intended to be wired in Delta, but is wired in wye would I expect to see more current for any given load (assuming motor is able to be started)
I am thinking that in a wye configuration the voltage at the motor is .58% of rated and therefore the torque is reduced to somewhere around 33% of rated. So since the torque is reduced shouldn't the motor be drawing higher current for any given loading on the motor under the new maximum avaliable torque value? Since the flux is reduced wont the motor try to make up for toque by pulling more current?
If the load now requires more than the new 33% rated torque value, wont the motor pull a higher than rated amount of current and trip?
So althgouh torque capability is reduced the motor will try to make up for it by pulling more current?