kwired
Electron manager
- NE Nebraska
- EC
As for line surges, I got to wire a $450,000 log home because its predecessor was burnt to the ground by a line surge.
What happened was (this from POCO engineers) a couple lines got crossed in a windstorm, fully saturating a transformer. When the lines came back apart, the transformer 'outrushed', surging the voltage on the lines for a few cycles. Enough to turn a night light into a fire. From there the fire spread to the curtains and shortly thereafter the entire log home was engulfed and destroyed.
The ground rods, obviously, were of no help. The new home is now outfitted with whole house surge protection.
As for Americans not having this grounding thing figured out yet, I have to agree. I get to see grounding from a different perspective than most, being a ham radio operator and all.
I can tell you that there are many myths about grounding that refuse to die. I can also tell you that most people can't explain the difference between bonding and grounding.
It's funny you bring up 'limit the voltage to ground'. I just had a conversation about that. If you read the entire passage, the reason for grounding is to limit the voltage between the ground and normally non-current carrying materials, such as metal enclosures and raceways.
While a rod or two will provide some limitation, they are poor choices for grounding electrodes. You have to realize that the NEC is a bare minimum. It's perfectly fine to use a more effective means of 'limiting', which is actually an attempt at equipotentiality.
Note the part of quote in bold. You are not going to eliminate surges from lightning you can help minimize them.
If the surge is on an ungrounded conductor grounding electrode does not directly protect the ungrounded conductor, surge protective devices will perform better however if there is a low impedance to shunt the surge to. Remember a ground rod of 25 ohms is a high impedance for a 120, or 277 volt source, but for lightning that is thousands of volts it is a low impedance.
There can be surges on POCO lines when there is switching occuring or like you said when there are faults on the line there can be resulting surges. They typically are not as destructive of a surge as lightning but is still a surge - the type that surge protective equiment silently protects you from. Another surge that happens at times is when POCO has transmission voltage line fail and fall on distribution lines. Seen the results of that a couple of times. Incident is quick like lightning but can cause damage in several homes and businesses if they are connected to the phase that had a rise in voltage there is a good chance they suffered some damage someplace.