Re: Individual branch Circuit?????
Thanks Don, For what it is worth I talked to a former chief editor of the NFPA-NEC Hand book and he thinks it is also a violation of 210.21 That the intent was 15 amp ocd ,15amp single receptacle.Use a #6 with pig tails but it is a 15 amp receptacle. 50 amp receptacle outlet 50 amp individual branch circuit.General rule.He compared this with the temp rating the lowest temp rating is what we must use. he called it the"weakest link approach"I mentioned field installations, He said make sure your insurance is paid.