Re: Individual branch Circuit?????
I?ve stayed away from this one long enough. I think I see where the mis-communication (for so I think this is) comes from. Marc: You need to remove the following statement from your pattern of logical reasoning, after which your argument will fall apart:
Originally posted by cram: A 50 amp receptacle is permitted to have a load of 50 amps.
This represents invalid logical reasoning. That is because you have used a word in two different contexts, in two different statements, within the same argument. What the NEC ?permits? in one context. What the manufacturer ?permits,? meaning the component?s published ratings, is another context.
Point in fact, the NEC does not ?permit? a 50 amp receptacle to carry 50 amps. What I mean is that you will not find in the NEC a statement to the effect that if anyone sees a 50 amp receptacle, then that person is ?permitted? to connect 50 amps worth of load to that receptacle. The NEC is (rightfully) silent with regard to the way the user uses the equipment. Once again, point in fact, the NEC is not addressed to, and does not govern, the user.
So if you have a 20 amp branch circuit (defined as having a 20 amp breaker), and if there is a 50 amp receptacle, the NEC does not ?permit? the connection of 50 amps of load. Rather, the NEC forbids the connection of over 16 amps of load (i.e., 80%, per 210.23(A)(1)). You are right to be concerned that the user might try to connect more load. For this reason, I would call it a bad design. But it is not a code violation.
Originally posted by cram: . . . a statement, it shall not be less, does not mean it can be anything greater.
Yes it does. Absolutely yes it does.