I have a vendor supplied system which includes a listed control panel (starter panel). The panel has a 1000A MCB, which feeds (2) separate 250 HP soft starters and other ancillary components. There are individual fuses (3P) feeding each soft start internal to the panel, then motor circuit conductors would go from the panel to the motor. The driven loads (250 HP compressors) are in the vicinity of the starter panel - both are outdoors under separate canopies - they could be arranged to be within site of the panel.
I had not originally considered that disconnects would be needed for the compressors, but I don't know that this meets any of the exceptions to 430.112. Although the compressors are part of the same system, they would not be considered to be part of the same machine or device. They are outdoors - not 'in the same room' as described in 430.112(c).
- Is there any other section that would apply to allow me to NOT specify individual disconnect switches for each motor?
- In the event that I need disconnects, does 430.109(E) allow us to use a 400A switch (rated 200HP, vs. a 600 A /400 HP switch) provided it is marked to not operate under load?
Obviously a couple extra 400A switches adds cost and takes up some real estate that I am not sure we have.
Thanks.
Thanks.