indoor hot tub
domnic
Electrical Contractor
On a indoor hot tub installed in doors must I use a insulated EGC ?
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
If it is residential install then you can use nm cable for the tub indoor. The only issue is if the manufacturer requires a full size equipment grounding conductor.
Buck Parrish
NC & IN
I had a guy install a full size outdoor type hot tub indoors and right in the middle of a small living room. You had like 4ft to walk around it to get to the front door. It was the craziest thing.
Yes... but to the OP . Is it in a hotel ?
domnic
It is in side ( residential ) any code reference PLEASE ?
domnic
try looking at 680.21 for the non insulated EGC in NM cable.
110.3(B) for when instructions require full sized EGC.
680-21-4 THANK YOU. no insulated egc required on inside residential hot tub. when using nm cable with egc in the cable.