I have been searching the web, codes and standards for more than two days looking for help and I feel frustrated. I need the grounding design requirements for a 13.8KV/480V substation located on an upper building floor. I have the IEEE Std 80-200 "IEEE GUIDE FOR SAFTY IN AC SUBSTAION GROUNDING" but this standard is mainly applicable for outdoor substations. In addition, the NEC falls short for this application. Has anyone come across this situation before?
 

bphgravity

Senior Member
Location
Florida
Re: Indoor Substation

Have you tried reviewing the current edition of the National Electrical Safety Code? This standard covers these requirements.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Re: Indoor Substation

Are you talking about indoor substations consisting of Metalclad and/or Metal enclosed switchgear?

If so, then I believe the NEC 250 grounding requirements are sufficient for 15kV just as they are for 600V.
 

bdarnell

Senior Member
Location
Indianapolis, IN
Occupation
Retired Engineer
Re: Indoor Substation

250 part X (10). Specifically starting at 250.180 applies to you, as well as any other applicable portions of 250. Part 10 supplements and modifies the rest of 250.
 