I asked an electrician to measure the voltage on the contorl wire in question with the wire lifted from the input. He found that witht the control station in the off position in the field, he measured 18V between the wire and ground with the wire lifted from the input.
This tells me that the capacitance coupling is coming from the hot wire that is going out to the control station since this is the only energized wire during this test.
I am trying to figure out why we saw 18V on this open circuit? I would expect that we saw more because there is now no current flow. Do we have to take current flow through the meter and thus the impedence of the meter into condiseration?
Is it possible to have 18V backfeed though the output contact in the overload relay? If you look at the control schematic you can see that when in local we have voltage on the secondary side of the relay output contact. Is it possible that 18V will backfeed through this contact? (We actually wired this starter a little different than shown in the schematic to where a backfeed across this contact would provide a direct connection to the input in question)
This tells me that the capacitance coupling is coming from the hot wire that is going out to the control station since this is the only energized wire during this test.
I am trying to figure out why we saw 18V on this open circuit? I would expect that we saw more because there is now no current flow. Do we have to take current flow through the meter and thus the impedence of the meter into condiseration?
Is it possible to have 18V backfeed though the output contact in the overload relay? If you look at the control schematic you can see that when in local we have voltage on the secondary side of the relay output contact. Is it possible that 18V will backfeed through this contact? (We actually wired this starter a little different than shown in the schematic to where a backfeed across this contact would provide a direct connection to the input in question)