ptonsparky
Tom
- EC - retired
Gars Hypothetical problem.
120 volt.
I have a switch 1500‘ from my PLC input. The ON voltage level of the input is > 60 v, min 5 ma. OFF is < 20 v, max 2 ma.
Two wire control via a #12 UF cable with 2 conductors and an EG.
Closing the switch gives an input. Opening the switch does not remove the input. Why?
(Real life problem before PLC)
2nd scenario.
The above cable is now in the same raceway with 480 volt conductors that become energized at the above input. 100 amps.
How does this affect the previous problem?
120 volt.
2nd scenario.