I'm seeing excessive heating on my line wires feeding large induction heaters. Looing for cause and remedy. Anything would help.
to induction heaters, 1500 kw and a 200 kw...wiring size is good... supplied with 6000A to gear. Seeing heating from heaters to transformer. wire by transformer at 100F by heater reading 130f. unit runs 24/7 temp measured with a flir infrared. some of the parts, like the bus way has hit 174f.How big are the heaters?
What is "excessive heating"? How did you measure it?
Are the wires undersized for the load?
Is the load drawing more or running longer than expected?
Ambient temperature is higher than expected?
As always, more detail about a problem is better than less.
Induction heating is a different breed of animal. Be sure to check NEC Art 665 especially 665.6. Often times grounding is unusual and standard grounding methods can cause excessive heating in raceways. You might also discuss the problem with the manufacturer as they often have solutuions.
It is 2 old pillar units....IT's been a while since I was involved but if I recall correctly we had to accomplish grounding via separate grounding conductors external to our conduit runs and insert non-metallic nipples to prevent the conduit from being a return path.
Lots of Code questions such as 300.3 and lots of discussions with a mfg rep who was also on CMP 12 which covers induction heating before it was all over with.
There are some strange current flows when dealing with this animal.
Who is the equipment manufacturer ?
Have you measured current (at all frequencies - true RMS, not a cheap meter) on those conductors during operation? Depending on the type of induction heating system and how it is fed, you can end up with high harmonic currents (or even excessive 60Hz current) due to resonant behavior with power factor correction capacitors upstream of the load. The temperatures you noted seem generally OK but if you're sure there's a problem to be solved then I'd start by checking the current with a meter that will show you what's really going on.
at 70% power both units combined pulling 3500 amps @ 480v
I made it about 3600A if the PF really is 0.4.Unless my math is wrong, that number is way too high. The total rated power for both units combined is 1700kW, right? So at 70% power you should be running around 1190kW which would be 1432A.
I made it about 3600A if the PF really is 0.4.
Perhaps you missed that from your calculations? That would account for your 1432A figure.
I calculated that PF of 0.4 based on the reported power and current numbers. That power factor can't be normal or acceptable for this equipment, can it?
I calculated that PF of 0.4 based on the reported power and current numbers. That power factor can't be normal or acceptable for this equipment, can it?
Ah, I see now. You did the calculation in reverse as it were. I did wonder about that.I calculated that PF of 0.4 based on the reported power and current numbers. That power factor can't be normal or acceptable for this equipment, can it?