Am concerned on engineering emt conduit for 3 and 4 way switches in a small commercial building.
The office area is only about 820 sq ft and the owner would like the lighting switched using snap switches from device boxes on three different entres in to the office.
Article 300.20 states information regarding induced currents in metal boxes and raceways.
I can route the 3way and 4way switches in a manner to include the neutral with the travelers to comply.
Maybe I am reading this too many times and am getting a bit apprehensive and concerned on which direction to take.
Lighting ckts are 120v.
Service is 120/208 3ph.
Any input would be appreciated.
Thank you