Inductor has no high inrush current

Status
Not open for further replies.

Ingenieur

Senior Member
Location
Earth
The math to work a numerical example is a pita
plus, it actually is an equation for a time varying i(t)
look at 4.2.8 IL(t) ... it is the equation for current in the L for an RLC ckt

we know that IL must be in amps
and that Vc(0) must be in volts
the e terms are unitless (s is in freq or 1/time and cancels time, unitless)
so the crap below Vc(0) must be Ohms

i= v/z
 

Sahib

Senior Member
Location
India
The math to work a numerical example is a pita
plus, it actually is an equation for a time varying i(t)
look at 4.2.8 IL(t) ... it is the equation for current in the L for an RLC ckt

we know that IL must be in amps
and that Vc(0) must be in volts
the e terms are unitless (s is in freq or 1/time and cancels time, unitless)
so the crap below Vc(0) must be Ohms

i= v/z
So the exponential factor in "e" is in equation 4.2.8 for current ie i not proportional to z and so ohm law does not hold during a transient
 

Ingenieur

Senior Member
Location
Earth
RL series ckt
assume V, R and L = 1

i(t) = 1 - e^-t
i(1) = 0.63 a
so v (1) across R = i x r = 0.63 x 1 = 0.63 v
vL = 1 - 0.63 = 0.37 v

i(1.5) = 0.78 a
v(1.5)R = 0.78 x 1 = 0.78 v
vL = 1 - 0.78 = 0.28 v


i(3) = 0.95 a
v(3)R = 0.95 x 1 = 0.95 v
vL = 1 - 0.95 = 0.05 v

as t > inf
i = 1 = v supply / (0 ohm L +1 Ohm R) = 1 a
vR = 1 x 1 = 1 v
vL = 0 as expected

Ohms law applies for a transient condition
same for RC AND RLC
math is more complicated
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
170923-1334 EDT

You may choose to call V = I*Z ohms law, I do not. When Ohm did his research it was based on DC thermocouple voltage, current and conductance of various conductive materials. Ohm's simple equation also works with an invariant resistance with a varying voltage or current.

Once you introduce inductance and/or capacitance the equation is not simple anymore except in special cases.

However, my purpose of this thread is to try to disassociate the concept of high inrush current, or high motor starting current from being caused because the load is being called inductive.

When a transformer is "turned on" a random high inrush current is not caused because the transformer looks to be inductive, but rather because you have a coil of wire around a ferromagnetic material that under certain conditions can be driven into core saturation causing the high current.

A high motor starting current does not occur just because the motor looks inductive, but rather from other factors. As examples: a starting coil that gets switched out near full speed, or in all cases the energy to accelerate the rotor.

An AC solenoid or contactor does not have a high inrush current because it looks inductive, but rather because its inductance changed from low to high following turn on.

That solenoid or contactor when used with DC has no inrush current even though the inductance changes. This can be a real advantage in a solenoid value because a stuck spool does not burnout the coil.

Generally you can not use an AC solenoid or contactor on DC because of design differences and get exactly the same results. An AC device can be used on DC at a lower voltage, but not the reverse. AC units have shading coils to produce a shifted magnetic field. The shading coil does not exist in a DC designed unit. Thus, DC units used on AC just chatter. Pull-in and holding currrents will be different. AC units have the advantage of high pull-in force with low holding power.

.
 

Besoeker

Senior Member
Location
UK
The transient is due to the switching of an ac signal
it is the ph angle
it is not dc per se
it is the extracted dc mathematical component of the total transient waveform
You mean the point on a sine wave at which it was switched in?
 

Ingenieur

Senior Member
Location
Earth
170923-1334 EDT

You may choose to call V = I*Z ohms law, I do not. When Ohm did his research it was based on DC thermocouple voltage, current and conductance of various conductive materials. Ohm's simple equation also works with an invariant resistance with a varying voltage or current.

Once you introduce inductance and/or capacitance the equation is not simple anymore except in special cases.

However, my purpose of this thread is to try to disassociate the concept of high inrush current, or high motor starting current from being caused because the load is being called inductive.

When a transformer is "turned on" a random high inrush current is not caused because the transformer looks to be inductive, but rather because you have a coil of wire around a ferromagnetic material that under certain conditions can be driven into core saturation causing the high current.

A high motor starting current does not occur just because the motor looks inductive, but rather from other factors. As examples: a starting coil that gets switched out near full speed, or in all cases the energy to accelerate the rotor.

An AC solenoid or contactor does not have a high inrush current because it looks inductive, but rather because its inductance changed from low to high following turn on.

That solenoid or contactor when used with DC has no inrush current even though the inductance changes. This can be a real advantage in a solenoid value because a stuck spool does not burnout the coil.

Generally you can not use an AC solenoid or contactor on DC because of design differences and get exactly the same results. An AC device can be used on DC at a lower voltage, but not the reverse. AC units have shading coils to produce a shifted magnetic field. The shading coil does not exist in a DC designed unit. Thus, DC units used on AC just chatter. Pull-in and holding currrents will be different. AC units have the advantage of high pull-in force with low holding power.

.

matters not what you nor I call it
v = iz hold true for transient analysis
 

Besoeker

Senior Member
Location
UK
Pull-in and holding currrents will be different. AC units have the advantage of high pull-in force with low holding power.
In olden days when DC controls were commonly used it was often the case that an economy resistor was switched in series with the coil of a DC contactor. Been there, done that.........:)
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
170923-1511 EDT

Fig. 3.2 above is a good illustration of the AC current in an RL switched AC circuit.

If you can visualize from this plot what happens if the time constant is very long and turn on occurs at a steady state current peak, then you can see why the upper limit of peak current is just 2 times the steady state peak.

.
 